Once and for all I want to make sure I am doing this correctly per NEC 430/440! Please see the attached CAD photo. I have a grouping of 4 exhaust fans on a remote section of the roof, where it would be somewhat of a waste to run separate feeds to each. So it is my intent to power them from one feed to a wireway. The motors are (1) 1.5 HP and (3) 1 HP. I will give 2 examples at different voltages just to be sure:
480V
3A * 1.25 + 2.1 + 2.1 + 2.1 = 10A
Minimum feeder size #12
MOCP (Panel Breaker) - 10A * 250% = 25A
208V
6.9A * 1.25 + 4.8 + 4.8 + 4.8 = 23A
Minimum feeder size #10
MOCP (Panel Breaker) - 23A * 250% = 60A
The real questions I have are as follows:
1) Did I size the breaker feeding the wireway correctly?
2) If the disconnects are fused, will that suffice for motor overload protection?
3) If motor overload is provided by default from the manufacturer, do those disconnects need to be fused?
4) Is this the best way to set up a system? And did I miss anything??
Thanks so much!
Keri

480V