multiple multiconductor tray cables in RMC help

Status
Not open for further replies.
Location
Texas
Occupation
electrical QC inspector
I'm looking for some direction on conduit fill when using multiple multiconductor tray cables in a RMC and PVC conduit. For example coming out of a box through the nipple into the cable tray, then going underground in PVC but with Rigid 90's and rigid above ground. Back to cable tray and then finally 1-3 tray cables in RMC to feed a skid with several motors on it. Also for some insight this is an industrial application outdoors in an oilfield facility. I have the overall diameter of wire from manufacturer (.294) for 16 awg single pair, and using chapter 9 table 4, 1.5" RMC is .829 at 40%. This is where I getting stuck. Or am I just not even in the same ballpark with the answer?
 
If the diameter (largest dimension) of the cable is 0.294", then the circular area of the cable is pi/4 * 0.2942 = .0678 in2. So if you allowed fill is 0.829 in2, you can fit up to 12 cables. (0.829 / 0.0678, rounded down).

Cheers, Wayne
 
If the diameter (largest dimension) of the cable is 0.294", then the circular area of the cable is pi/4 * 0.2942 = .0678 in2. So if you allowed fill is 0.829 in2, you can fit up to 12 cables. (0.829 / 0.0678, rounded down).

Cheers, Wayne
I knew I was missing the last piece of the puzzle. Thank you so much. Also I'm assuming that formula should work if I plug in different numbers according to the specs?
 
I knew I was missing the last piece of the puzzle. Thank you so much. Also I'm assuming that formula should work if I plug in different numbers according to the specs?
Yes, the area of a circle will always be "pi * diameter squared /4."

For further details and important clarifications, see Chapter 9 Table 1 and all its notes.

Cheers, Wayne
 