TexMasterElectrician
Member
- Location
- Texas
- Occupation
- electrical QC inspector
I'm looking for some direction on conduit fill when using multiple multiconductor tray cables in a RMC and PVC conduit. For example coming out of a box through the nipple into the cable tray, then going underground in PVC but with Rigid 90's and rigid above ground. Back to cable tray and then finally 1-3 tray cables in RMC to feed a skid with several motors on it. Also for some insight this is an industrial application outdoors in an oilfield facility. I have the overall diameter of wire from manufacturer (.294) for 16 awg single pair, and using chapter 9 table 4, 1.5" RMC is .829 at 40%. This is where I getting stuck. Or am I just not even in the same ballpark with the answer?