Jawrenn18
Member
- Location
- Charleston SC
Good afternoon,
I'm in a bind on a project. 800 amp single phase home. 9000 sqft heated and cooled. We were supposed to be installing an 800 amp transfer switch in an assembly with 800 amp main breaker and 4 200 amp breakers. I was notified that the enclosure would not be available until late this year. I got with my supplier and he recommended installing 1 800 amp disconnect, feeding each 200 amp panel from it and installing main breakers in the panels. I've looked at code 408.36 and it seems that this would be permissible. 408.36 references 230.71which states not more than 6 disconnects on the building. I've done this on a few commercial projects with no issue. Just making sure this isn't going to bite me in the behind come final inspection time. The inspectors for this job show up in packs of 3-5 and bring their code books.
I'm in a bind on a project. 800 amp single phase home. 9000 sqft heated and cooled. We were supposed to be installing an 800 amp transfer switch in an assembly with 800 amp main breaker and 4 200 amp breakers. I was notified that the enclosure would not be available until late this year. I got with my supplier and he recommended installing 1 800 amp disconnect, feeding each 200 amp panel from it and installing main breakers in the panels. I've looked at code 408.36 and it seems that this would be permissible. 408.36 references 230.71which states not more than 6 disconnects on the building. I've done this on a few commercial projects with no issue. Just making sure this isn't going to bite me in the behind come final inspection time. The inspectors for this job show up in packs of 3-5 and bring their code books.