Carultch
Senior Member
- Location
- Massachusetts
I've got a job where what got built doesn't match what was on the drawing set. Instead of the correct single wire, double ground wires each individually of an insufficient size were installed. The wires are in the same conduit. The two ground wires do both "add up to" what you would need, both in terms of adding the amp values in Table 250.122, and in terms of adding up the KCMIL.
Anyone know of any code reference that would allow this? I'd rather not have the debate if I don't have to.
My understanding is that it is not correct. My understanding is that no matter what the situation of paralleling, if an EGC wire is installed, all conduits need a full size equipment ground wire that can carry the fault current on its own.
Example: a 200A circuit, with a #6 Cu ground specified, but with two #6 Al grounds installed instead.
#6 AL is rated to be the ground wire of up to 100 A, and intuitively one might think that 2 parallel #6 AL grounds could be rated for 200A. And the KCMIL add up as well, since 2 x #6 is the same kcmil as a #3.
Anyone know of any code reference that would allow this? I'd rather not have the debate if I don't have to.
My understanding is that it is not correct. My understanding is that no matter what the situation of paralleling, if an EGC wire is installed, all conduits need a full size equipment ground wire that can carry the fault current on its own.
Example: a 200A circuit, with a #6 Cu ground specified, but with two #6 Al grounds installed instead.
#6 AL is rated to be the ground wire of up to 100 A, and intuitively one might think that 2 parallel #6 AL grounds could be rated for 200A. And the KCMIL add up as well, since 2 x #6 is the same kcmil as a #3.