Been a lurker for years as a Mechanical Designer/Facility Manager, and this site has been great for the occasional reference data.
Have a little more involved question.
Can a Hospital (with a Type 1 Electrical System), ALSO be fed power from another, completely independent Type 1 Electrical System?
At this facility (where I used to work as the Facility Manager), the Electrical Engineer (from an A/E) is recommending that a new ICU expansion/remodel be fed from a new Central Plant, with a new Electrical System. The Central Plant was originally to be powered from an attached and dedicated 480v system, which would remove appx 1200A (old chillers on the equipment branch) from the almost overloaded 208v system. My recommendation to the owner was to build the plant, take the load off the existing 208v system and use that extra capacity to power the ICU expansion. Yes, some switchgear work would be required as the Chillers are on the Equipment Branch, and we will need more capacity on the LS and Critical Branches as well; but the existing switchgear is only about 10 years old, so parts should not be a problem.
The Electrical Engineers plan will have the facility served by (2) isolated electrical systems, each Type 1.
To me, this seems problematic. I have spoken to the Electrical Engineer, and he insists there are no code problems with this.
While there may not be code issues, as the former Facility Manager this gives me cause for concern.
Outlets 20 feet away from each other - and within line of sight - will be on a different system.
Controls (with sensors and power supplies spread over a vast area) may have connections to both 208v systems.
In an emergency, shutting off power will be...more complicated.
I can envision construction workers running power cords to "available" outlets, with power tools connected to the different systems easily in contact.
The potential for cross connecting will ALWAYS be there; say, Contractor "A" extends a light on the new system, and then Contracator "B" extends a light from an adjacent area on the old system, and they are right next to each other. This does not seem a good idea.
So. Am I being chicken little here? Or is this truly a bad idea, notwithstanding "there is not a violation of NEC". If there is a NEC conflict, I would sincerely appreciate a pointer.
TIA
Have a little more involved question.
Can a Hospital (with a Type 1 Electrical System), ALSO be fed power from another, completely independent Type 1 Electrical System?
At this facility (where I used to work as the Facility Manager), the Electrical Engineer (from an A/E) is recommending that a new ICU expansion/remodel be fed from a new Central Plant, with a new Electrical System. The Central Plant was originally to be powered from an attached and dedicated 480v system, which would remove appx 1200A (old chillers on the equipment branch) from the almost overloaded 208v system. My recommendation to the owner was to build the plant, take the load off the existing 208v system and use that extra capacity to power the ICU expansion. Yes, some switchgear work would be required as the Chillers are on the Equipment Branch, and we will need more capacity on the LS and Critical Branches as well; but the existing switchgear is only about 10 years old, so parts should not be a problem.
The Electrical Engineers plan will have the facility served by (2) isolated electrical systems, each Type 1.
To me, this seems problematic. I have spoken to the Electrical Engineer, and he insists there are no code problems with this.
While there may not be code issues, as the former Facility Manager this gives me cause for concern.
Outlets 20 feet away from each other - and within line of sight - will be on a different system.
Controls (with sensors and power supplies spread over a vast area) may have connections to both 208v systems.
In an emergency, shutting off power will be...more complicated.
I can envision construction workers running power cords to "available" outlets, with power tools connected to the different systems easily in contact.
The potential for cross connecting will ALWAYS be there; say, Contractor "A" extends a light on the new system, and then Contracator "B" extends a light from an adjacent area on the old system, and they are right next to each other. This does not seem a good idea.
So. Am I being chicken little here? Or is this truly a bad idea, notwithstanding "there is not a violation of NEC". If there is a NEC conflict, I would sincerely appreciate a pointer.