Hi Guys,

If I have 12- #12current carrying conductors in a 2" pipe (multiwire 3 phase) do I need to consider derateing? I know that I am not close to my conduit fill, but I am concerned about ampacity.

Can 350 AWG be paralleled for an 800amp service?

Where online can I find GE product 3phase reasonably priced.

Thanks
 

Attachments

  • image.jpg
    image.jpg
    136.1 KB · Views: 0
  • image.jpg
    image.jpg
    138.7 KB · Views: 0
  • image.jpg
    image.jpg
    142.5 KB · Views: 0
Hi Guys,

If I have 12- #12current carrying conductors in a 2" pipe (multiwire 3 phase) do I need to consider derateing? I know that I am not close to my conduit fill, but I am concerned about ampacity.

Can 350 AWG be paralleled for an 800amp service?

Where online can I find GE product 3phase reasonably priced.

Thanks

Yes.
Yes.
Not sure just keep looking.
 
Hi Guys,

If I have 12- #12current carrying conductors in a 2" pipe (multiwire 3 phase) do I need to consider derateing? I know that I am not close to my conduit fill, but I am concerned about ampacity. Table 310.15B2a does not mention conduit size.

Can 350 AWG be paralleled for an 800amp service? 620 amps is a long way from 800 amps.

Where online can I find GE product 3phase reasonably priced.

Thanks

Thanks
 
I didn't run the conduit or pull the wires. Should I break up the circuits into runs of 12/4 because I will have to increase wire sizes with current scheme otherwise?
 
Can 350 AWG be paralleled for an 800amp service?
No. If the calculated load is less than 620 amps, then you can use a pair of 350's. However, you have to protect the service with an OCPD no higher than 700 amps (i.e., the next standard size that is higher than 620).
 
I didn't run the conduit or pull the wires. Should I break up the circuits into runs of 12/4 because I will have to increase wire sizes with current scheme otherwise?
Not so fast, if you please. I need clarification. If you are dealing with three circuits, each a MWBC consisting of three phase conductors and a neutral conductor, then you are not necessarily dealing with 12 current-carrying conductors. If there are no significant harmonic loads on these circuits, then you only have nine current-carrying conductors. In that case, a #12 THHN derates from 30 amps down to 21 amps. Therefore, you can still use a #12 with a 20 amp breaker. So you could put all 12 wires (plus the EGC) in the same conduit.
 