An electrician installed a 20 amp receptacle circuit (not multiwire) with 6 recepts., #12 wire, and 15 amp duplex receptacles. He wired them as feed thru (daisy chain) usin the 4 screws on the recept.
The inspector would not accept it. Said he had to splice the wires and leave a pig tail to connect to only 2 screws of the recept.
I cannot find anything like this in the NEC. 210.21 (B)(3) allows the 15 amp recept. 300.13 (B) covering continuity of the grounded conductor only applies to multiwire circuits. Any comments?