Basic scenario: A 600 amp service comprised of a parallel set of 350s with Polaris taps in a wireway and (3) individual 3/0s supplying 3 200 amp service disconnects.
Option 1:
Service lateral supplying wireway tapped to (3) adjacent disconnects on the outside of the building which supply feeders to interior panels.
Option 2:
Service Lateral consist of 2 exterior conduits with LBs that penetrate the exterior wall immediately entering an interior wireway with Service rated polaris connectors
and 3/0 conductors to M/B panels at the wireway.
The argument is being made that Option 2 is a violation of 230.90 as the 350s are required to terminate in a (single) OCP device once they enter the building.
Seemingly 230.90 exception 3 would allow either option.
On a non-dwelling structure, will Option 1 and 2 both be allowed per the 2107 and 2023 NEC, ??
(All grounding is to Code..only question relates to 230.90)