I have an existing industrial facility with two older 2000 amp (277/480 volt) service entrances and a newer (circa 1999) 3000 amp service entrance. The 3000 amp service was installed to serve new processes and was installed in the same area of the plant as the new processes, away from the older electrical room that houses the other two services. The two older services are heavily loaded, and the connected load on the 3000 amp service is only about 450 KW. The AHJ is reluctant to allow us to remove load from the existing services and refeed from the 3000 amp service, and he cites the safety issues involved with having power from multiple services serving equipment within the same area of the plant. The plant maintenance personnel are highly qualified and familiar with the plant. All services are labeled and have floor plan plaques showing locations of other services. All equipment will be labeled as to the source service. We have agreed to the AHJ's requirements for pushbuttons at the service entrance mains that would allow disconnection of the other (remote) services through shunt trip.
I feel that if load is divided in a clear, sensible, logical manner, there should be no violation of code or safety concerns.
Any comment on code violations or safety concerns?
I feel that if load is divided in a clear, sensible, logical manner, there should be no violation of code or safety concerns.
Any comment on code violations or safety concerns?