I'm looking at at an industrial building with 4 services. Assume that the multiple services are permitted in accordance with the exceptions of 230.2. Three of the shunt-trip discos for these services, however, are located at various external locations of the building and one is inside but close to an entrance. Assume further that these discos are identified as required by 230.2(E). My question is the following. It seems to me that the discos ought to be grouped close to one another because IMHO it would be unreasonable for responders to an emergency to have to run around the building and read the various plaques but I cannot find an NEC requirement that I can use to justify this. The reference to 225.37 doesn't address grouping specifically and in any event 225.34 addresses branch circuits and feeders, not services. Can you help by pointing me to requirement(s) I can use or should I just accept it and let the fire marshal worry about it? I don't think that's the best option because it implies that the NEC accepts a situation that I would deem as unsafe.
I look forward to your wisdom, as usual.
Heinz R.