hbendillo
Senior Member
- Location
- South carolina
I have a hospital facility that has three services. The newest service at a patient tower was done according to currrent codes. Generator, three branches, everything separated and fed according to code requirements. 480-volt, three-phase, 2000 amps. The other two services consist of one transfer switch each and branch circuits and feeders not seperated according to branch or use downstream of the transfer switch. Both of these are 208-volt, three-phase. One is 2000 amps I think and the other 4000 amps. The 4000 amp service feeds a significant part of the existing hospital including the emergency department and radiology. Because of the increasing demand for radiology and mechanical systems loads we recently installed a separate 1600-amp 480-volt service to handle the demand. Well, now every time the owner adds large loads anywhere on the site he wants them fed at 480-volts. This includes the part of the building and service that has no 480-volt component. What are the rules for feeding equipment in one part of the facility, with it's own service, from another part of the building with it's own service. Besides not being good engineering practice in my opinion, what does the code say about it? Oh, he does this with both emergency and normal power loads.