Multiple services to a structure

Status
Not open for further replies.
Would multiple services into a building need to be grouped at the same point or shunt tripped?

There is no requirement for shunt tripping of services.

The code does not seem to require the disconnecting means from different services to be grouped together.
 
But they just must not exceed 6, correct?
There can be no more than six service disconnects grouped at a common location. If the service disconnects are not grouped, each set of service entrance conductors can have up to six disconnects.
 