zclawz
Member
- Location
- Denver, CO
- Occupation
- Electrical Engineer
I am reviewing an existing installation of a 3500ft run of (3) sets of #6 4.16kV conductors (airfield lighting cable) installed in a single 4" conduit. There is a short along the conductors length that is bringing up the review of the existing conditions. The owner has a recieved a proposal to replace the existing conductors with new appropiate conductors or reuse the existing conductors and provide repairs where needed. Both proposals utilize a single conduit with multiple sets of conductors.
Reviewing 2017 NEC 310.60 the code does not expressly dictate if multiple conductors can share the same conduit. Reviewing the work with a local contractor they have installed a set of (3) 4.16kV conductors in a single conduit on previous projects but never multiple sets. They were not confident the installation of (3) sets of conductors would even be code compliant. Is it possible to have multiple sets of conductors at 4.16kV sharing the same conduit? If so what deration factor should be assumed (a table like 310.15(B)(3)(a) is not provided for 2001-35000V conductors)?
To replace the conductors with new and replace underground pullboxes along the route would cost the owner 250k. Adding additional parallel conduits along the 3500ft run into extremely rocky soil would cost the owner multiple hundreds of thousands of dollars. If possible I would like to limit the additional cost on the owner. Thanks
Reviewing 2017 NEC 310.60 the code does not expressly dictate if multiple conductors can share the same conduit. Reviewing the work with a local contractor they have installed a set of (3) 4.16kV conductors in a single conduit on previous projects but never multiple sets. They were not confident the installation of (3) sets of conductors would even be code compliant. Is it possible to have multiple sets of conductors at 4.16kV sharing the same conduit? If so what deration factor should be assumed (a table like 310.15(B)(3)(a) is not provided for 2001-35000V conductors)?
To replace the conductors with new and replace underground pullboxes along the route would cost the owner 250k. Adding additional parallel conduits along the 3500ft run into extremely rocky soil would cost the owner multiple hundreds of thousands of dollars. If possible I would like to limit the additional cost on the owner. Thanks