nzubrzycki
Member
- Location
- Orlando, FL
1) I'm working on a building where the fire pump ats/controller is multiple-fed by a normal source (secondary tap of service transformer) and a stand-by generator source. Per NEC 695.6 (A) exception, am I required to concrete encase or 2-hour protect ONLY the conductors on the load side of the ATS? Or am I supposed to protect the normal and emergency feeds as well? The way I read the exception, it seems to me that if using multiple sources to feed the fire pump, then only the conductors on the load side of the transfer switch have to be protected by means of concrete encasement or 2-hr fire rated wiring.
2) Is MI cable considered a 2-hour rated assembly?
3) Am I required to provide a supervised disconnect or is this optional per 695.4 (B) (i.e. "shall be permitted" to me sounds like it's optional).
Thanks