Gentlemen?and ladies?
I?m one of those dastardly home inspectors. At the risk of incurring your wrath I have a question. Basically it's: How many splices are you comfortable with for a GEC between the panel and ground rod?
Here?s the situation: 1907 house that had the wiring partially updated in the 70?s. This included a ?modern? 200 amp service panel. Grounding was accomplished with a #4 conductor to the water pipe entrance. Then in 1987 a ?carriage house? with separate living quarters was built at the street connected to the main house by a 30? breezeway. There are now two service drops to the property, two meters etc. Both service panels are now in the garage of the addition, one a normal distribution panel serving the carriage house, the other just a single 200 amp disconnect for the main house. Both of these are connected to a single ground rod. Three insulated feeders (2 hot, 1 neutral) are then run from the disconnect. through metallic conduit to a new ?service? mast at the back of the garage, overhead (30+ foot span with a bare support cable) to the ?original? service mast at the main house, through the old meter base and to the panel which is now a sub-panel. This panel had a new ground bar added, the bonding strap disconnected, and the grounds and neutrals separated?all correct. The conductor to the water piping was abandoned at the panel (no bonding at present other than by accidental contact between this original GEC and other grounding conductors).
So now the grounding electrode is about 100 feet away and the effective GEC is a mishmash of conduit, support wire, and jumpers. While all connections look like they have been made correctly with appropriate fittings and jumpers I sure would have been happier seeing a continuous bare fourth conductor run between the disconnect and panel. While I didn?t report this as wrong (it seems to be allowed) I did recommend that the client get an evaluation of this ?GEC? from the electrician while he?s there fixing the other problems. If the water piping is bonded (as per my recommendation) it seems that that would become the path of least resistance and would once again effectively be the grounding electrode.
I?m not asking for an evaluation of this particular installation (that is hopefully going to be done) so much as your general thoughts on this for my own illumination.
Richard Moore
Seattle, WA
[ January 20, 2004, 02:53 PM: Message edited by: richardmoore ]
I?m one of those dastardly home inspectors. At the risk of incurring your wrath I have a question. Basically it's: How many splices are you comfortable with for a GEC between the panel and ground rod?
Here?s the situation: 1907 house that had the wiring partially updated in the 70?s. This included a ?modern? 200 amp service panel. Grounding was accomplished with a #4 conductor to the water pipe entrance. Then in 1987 a ?carriage house? with separate living quarters was built at the street connected to the main house by a 30? breezeway. There are now two service drops to the property, two meters etc. Both service panels are now in the garage of the addition, one a normal distribution panel serving the carriage house, the other just a single 200 amp disconnect for the main house. Both of these are connected to a single ground rod. Three insulated feeders (2 hot, 1 neutral) are then run from the disconnect. through metallic conduit to a new ?service? mast at the back of the garage, overhead (30+ foot span with a bare support cable) to the ?original? service mast at the main house, through the old meter base and to the panel which is now a sub-panel. This panel had a new ground bar added, the bonding strap disconnected, and the grounds and neutrals separated?all correct. The conductor to the water piping was abandoned at the panel (no bonding at present other than by accidental contact between this original GEC and other grounding conductors).
So now the grounding electrode is about 100 feet away and the effective GEC is a mishmash of conduit, support wire, and jumpers. While all connections look like they have been made correctly with appropriate fittings and jumpers I sure would have been happier seeing a continuous bare fourth conductor run between the disconnect and panel. While I didn?t report this as wrong (it seems to be allowed) I did recommend that the client get an evaluation of this ?GEC? from the electrician while he?s there fixing the other problems. If the water piping is bonded (as per my recommendation) it seems that that would become the path of least resistance and would once again effectively be the grounding electrode.
I?m not asking for an evaluation of this particular installation (that is hopefully going to be done) so much as your general thoughts on this for my own illumination.
Richard Moore