NewtonLaw
Senior Member
- Location
- Honesdale, PA USA
Thank you for your response. The circuits are the same size but different lengths of 500 MCM CU.It depends on the wire size. If each has an ampacity of 400 amps or greater, then you don't have a tap you have a feeder. If they are less than 400 amps you need to comply with one of the tap rules in 240.21. curious how you can physically land 2 400 amp sets on a 400 amp CB? I guess 500 cu would work using next size up rule.
I would think he would have a splice box outside the MDP using Polaris or Ilsco type splices.It depends on the wire size. If each has an ampacity of 400 amps or greater, then you don't have a tap you have a feeder. If they are less than 400 amps you need to comply with one of the tap rules in 240.21. curious how you can physically land 2 400 amp sets on a 400 amp CB? I guess 500 cu would work using next size up rule.
Yeah I'm trying to remember what I have seen in the past, but lugs that take 2-500's does seem unlikely. IIRC the last 400 amp frame breaker I used was an I-line and it had single ports, but they could take two conductors, but I doubt as big as 2 500's. Siemens 400A MLO panel boards have two hole lugs, a large and a small, but the smaller one only went up to 350 I believe.I would think he would have a splice box outside the MDP using Polaris or Ilsco type splices.
It depends on the wire size. If each has an ampacity of 400 amps or greater, then you don't have a tap you have a feeder. If they are less than 400 amps you need to comply with one of the tap rules in 240.21. curious how you can physically land 2 400 amp sets on a 400 amp CB? I guess 500 cu would work using next size up rule.
Take the 600kcmil/250kcmil "snowman lug" off the breaker. Replace it with a double 600 kcmil lug.
Terminals on large CB's are designed to be interchanged as long as you replace them with the proper listed terminals. We reconfigure them quite often.