I have a commercial customer with 36 test stations, each station will have the following quantity of receptacles:
2 - 50A, 208V, 3ph Nema 15-50R
2 - 20A, 120V, 1ph Neam 5-20R (Quad)
1 - 20A, 380V, 3ph Nema L16-20R
1 - 30A, 480V, 3ph, Nema L16-30R
1 - 30A, 208V, 1ph, Nema 10-30R
They will not be using more than one of the receptacles at a time, with the exception of the quads.
Also, it is unlikely that all the stations will be used at the same time. And if they are, very unlikely they will all be using the same voltage receptacle.
Any suggestions on diversity or demand? My service size is HUGE because I can't figure out a way to demand down these loads.
Thanks,
Par38lamp