I have a steel building devided into 4 units each with its own service and water service. The panels are all feed with 4/0 ser from a 4 stack meter having breaker disconnect inside it for each 200.I drove a ground rod and ran a 2/0 alum to water service 1 as per 250.66 for a 640amp cal load but what the hell do i run to other water services.
are they supplimental 250.66A ,250.53E #6 from each bay panel to its own water supply
are they each there own water pipe and need a 2/0 to each from meter stack ( not enough lugs)
are the falling under 250.104-2 in which case it would be a #4 to each pipe from the panel in that unit. but there are all metel pipes in each they are not connected as i did a ohm check. so outside somewere there is plastic or other
help please