Hey guys,
A contractor wants to group (4) VAVs (heat only, 5kW each) together and feed it from one circuit breaker 208V, 3phase.
Total load would be 20 kW which i calculate to be around 56A load.
He wants to use a 70A circuit breaker which would require #4AWG.
My concern is he would have to run #4AWG's to each of the 4 VAV boxes correct? He would not be allowed to tap down to a smaller guage wire to feed one of the VAVs, right? The VAV's come with an integral disconnect which is non-fused.
All of these 5kW VAV's are 208V, 3phase. Is it wise to group these together and feed from one larger breaker? It seems like it would be more expensive this way?? Bigger breaker, bigger wire. But on the other hand you are saving panel space....