We are looking at a preliminary design where a customer will have several VFD's ranging from 75Hp all the way up to 450Hp at 480V fed from Bus Duct in their facility. The Bus Ducts will likely be fed from Switchgear breakers and the bus duct will be used to allow the customer the flexibility off easily adding drives to the process as necessary.
This particular customer rents space in their facility and provides the availability for their customers to connect drives to their system as needed for the particular application area the space is rented for. So with that said there is not an exact count of the drives that will be installed on the Bus Duct and thus the customers will add the drives as their customers rent space in the facility. The customer has provided us with a rough count of drives and drive sizes for another part of their facility which is similar. Most of these drives will be operating at high frequencies (450HZ or so...so likely not large motor loads) but some of these drives are in the 400 and 450HP range.
I was curious how others would go about the load calculations for this application since the size and quantity of the drives are not fixed but rather will be added as necessary. Would you simply provide Bus Duct feeders from switchgear with each feeder sized for a maximum HP total to allow the drives to be added as needed up to the HP Total? Or would you use the similar existing drive counts/sizes as the basis for sizing feeders with each feeder being specified for a particular drive size & count? Obviously the large 400 and 450HP drives can have a large impact on some of the feeder sizing so I was just curious what approaches others would taking to laying out this distribution.
Curious to hear other considerations for this application.
Thanks
This particular customer rents space in their facility and provides the availability for their customers to connect drives to their system as needed for the particular application area the space is rented for. So with that said there is not an exact count of the drives that will be installed on the Bus Duct and thus the customers will add the drives as their customers rent space in the facility. The customer has provided us with a rough count of drives and drive sizes for another part of their facility which is similar. Most of these drives will be operating at high frequencies (450HZ or so...so likely not large motor loads) but some of these drives are in the 400 and 450HP range.
I was curious how others would go about the load calculations for this application since the size and quantity of the drives are not fixed but rather will be added as necessary. Would you simply provide Bus Duct feeders from switchgear with each feeder sized for a maximum HP total to allow the drives to be added as needed up to the HP Total? Or would you use the similar existing drive counts/sizes as the basis for sizing feeders with each feeder being specified for a particular drive size & count? Obviously the large 400 and 450HP drives can have a large impact on some of the feeder sizing so I was just curious what approaches others would taking to laying out this distribution.
Curious to hear other considerations for this application.
Thanks