rlane00
Member
- Location
- Clackamas, OR
- Occupation
- Electrical Contractor, Supervising Electrician, EE
We have a 12-unit multi-family building with a single 800 amp service (ganged meters) and three separate metal water pipes stubbed up into the building. One pipe is for the sprinkler system and the other two are for the 12 units, but are converted to plastic within a few feet of stubbing up from the floor and distributed to each unit from there.
My question is how to run GEC and/or bonding. Per 250.66 I need 3/0 copper for the GEC, but I'm not sure if I need to run this to all three of the water pipes, or to just one (the closest to the service) and then bond the other two. Based on 250.104(A)2 it appears that I can just bond the other two (using #8 since each unit has 100 amp OCPD) to the panelboard for that occupancy - but the water pipes are not supplying a single occupancy so I'm not sure if this section applies.
I searched this site and found a similar thread http://forums.mikeholt.com/showthread.php?t=79699&highlight=multiple+water+pipe from 2006, but would appreciate some current feedback. Thanks.
My question is how to run GEC and/or bonding. Per 250.66 I need 3/0 copper for the GEC, but I'm not sure if I need to run this to all three of the water pipes, or to just one (the closest to the service) and then bond the other two. Based on 250.104(A)2 it appears that I can just bond the other two (using #8 since each unit has 100 amp OCPD) to the panelboard for that occupancy - but the water pipes are not supplying a single occupancy so I'm not sure if this section applies.
I searched this site and found a similar thread http://forums.mikeholt.com/showthread.php?t=79699&highlight=multiple+water+pipe from 2006, but would appreciate some current feedback. Thanks.