delectric123
Senior Member
- Location
- South Dakota
I am making an electrical installation consisting of 12 - ventilating fans operating on 240 Volts 3 Phase with each fan motor having a FLA rating of 4.2 A. These fans are all approximately 200 ft. away from the control room. In the control room, the breaker panel is about 10 ft. away from the contactor boxes? The contactor boxes are factory assembled with each box housing 4 contactors with thermal overloads. The boxes are wired for connection to one breaker. Would a 20 amp breaker be permissible?If a 20 amp is allowed, and I?d use 12 AWG wire for going to all the fans, would it be allowed to have all the wires(36 current-carrying conductors) in the same raceway?(PVC conduit)