S spsnyder Senior Member Jun 21, 2012 #1 Does the NEC allow multiple wires under a single lug of an ATS. We need to tap the conductors and there is room under the lug. Thanks.
Does the NEC allow multiple wires under a single lug of an ATS. We need to tap the conductors and there is room under the lug. Thanks.
J John120/240 Senior Member Location Olathe, Kansas Jun 21, 2012 #2 Is the lug listed for multiple wires ? There may be other reasons why or why not you can do this.
qcroanoke Sometimes I don't know if I'm the boxer or the bag Location Roanoke, VA. Occupation Sorta retired........ Jun 21, 2012 #4 spsnyder said: The lug is not listed for multiple wires. Thank you. Click to expand... Then you cannot do what you are asking. you could swap out the lugs for lugs rated for what you want to do or you could do a splitbolt or c-tap. You need to look at tap rules also.
spsnyder said: The lug is not listed for multiple wires. Thank you. Click to expand... Then you cannot do what you are asking. you could swap out the lugs for lugs rated for what you want to do or you could do a splitbolt or c-tap. You need to look at tap rules also.