MNSparky
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Contractor - 2023 NEC
I was reading my "Mike Holt Changes to the NEC - 2017 edition" and 210.4(C) Ex 2 was discussed. It clearly states in that book that it is acceptable to have line to line and line to neutral loads on the same multiwire BC where all ungrounded conductors are opened simultaneously by the OCPD. Pg 57 if you have the book.
Ive been told in the past by an AHJ that I can't do this due to "mixed loads". He didn't want the two ungrounded conductors to be unbalanced. I've never been able to prove him wrong as the actual wording in 210.4(C) Ex 2 infers, IMO, that line to line loads that use a neutral (like a clothes dryer or range) are acceptable. It doesn't say anything about mixed loads.
My question in the past was in reference to attic air handling units in residential applications. We do these a lot, where a house with boiler heat wants AC as well. The HVAC contractor puts a condenser outside on the ground and runs their lineset to the attic to a 240v air handler. My question is why can't I run a multiwire branch circuit to the attic and supply the air handler and the required 120v service lighting and receptacle off that same MWBC? There's a disconnect at the air handler so the service tech shouldn't have to shut off the circuit to service, thus loosing the lights and receptacle. Am I missing something?
Ive been told in the past by an AHJ that I can't do this due to "mixed loads". He didn't want the two ungrounded conductors to be unbalanced. I've never been able to prove him wrong as the actual wording in 210.4(C) Ex 2 infers, IMO, that line to line loads that use a neutral (like a clothes dryer or range) are acceptable. It doesn't say anything about mixed loads.
My question in the past was in reference to attic air handling units in residential applications. We do these a lot, where a house with boiler heat wants AC as well. The HVAC contractor puts a condenser outside on the ground and runs their lineset to the attic to a 240v air handler. My question is why can't I run a multiwire branch circuit to the attic and supply the air handler and the required 120v service lighting and receptacle off that same MWBC? There's a disconnect at the air handler so the service tech shouldn't have to shut off the circuit to service, thus loosing the lights and receptacle. Am I missing something?