This has probably been beaten to death.
I recently replaced a 200 amp single phase residential panel. The panel had multiple multiwire branch circuits, at the time, (FWIW none of which terminate on a common yoke).
I couldn't get enough pole breakers so I installed two single pole CB's with a nail for a handle tie for each MWBC. (I've never had an issue with this in the past)
The inspector is insisting I replace the single CB's with two pole CB's.
I told him I shouldn't have to replace them. I mentioned 210.4 (4) (it has a simultaneous disconnect) and 240.15 (B)(1) (two single-pole individual breakers, with identified handle ties) I'm not quite sure what is meant by identified handle tie it's pretty self explanatory as is.
His argument is that it won't trip simultaneously, which I can also see his point.
Bottom line: Am I wrong?
I recently replaced a 200 amp single phase residential panel. The panel had multiple multiwire branch circuits, at the time, (FWIW none of which terminate on a common yoke).
I couldn't get enough pole breakers so I installed two single pole CB's with a nail for a handle tie for each MWBC. (I've never had an issue with this in the past)
The inspector is insisting I replace the single CB's with two pole CB's.
I told him I shouldn't have to replace them. I mentioned 210.4 (4) (it has a simultaneous disconnect) and 240.15 (B)(1) (two single-pole individual breakers, with identified handle ties) I'm not quite sure what is meant by identified handle tie it's pretty self explanatory as is.
His argument is that it won't trip simultaneously, which I can also see his point.
Bottom line: Am I wrong?