I ran into a situation where the two lines of a multiwire branch circuit are connected the two connections of a tandem circuit breaker.
Correct me if I say anything wrong:
The two lines, that share a neutral, should be connected to different phases/legs.
The connection should be to a two pole circuit breaker so both circuits disconnect/open together.
Suppose if the two circuits served loads in a dwelling unit and assuming the required number of circuits were still met and the total connected load were OK could the two lines be connected to one circuit breaker (one circuit). This one bothers me because there would be two hot wires connected to the same phase and one neutral in the same cable. On the other hand the sum of the load on the two lines would equal the load on the neutral.
Correct me if I say anything wrong:
The two lines, that share a neutral, should be connected to different phases/legs.
The connection should be to a two pole circuit breaker so both circuits disconnect/open together.
Suppose if the two circuits served loads in a dwelling unit and assuming the required number of circuits were still met and the total connected load were OK could the two lines be connected to one circuit breaker (one circuit). This one bothers me because there would be two hot wires connected to the same phase and one neutral in the same cable. On the other hand the sum of the load on the two lines would equal the load on the neutral.