Please explain in detail where and how a multiwire branch circuit may be used. Can the neutral conductor in a 4-wire NM cable (black, red, white, bare ground) be shared between the two energized circuit conductors?
While two pole breakers are permitted, they are not required for multiwire circuits. The rule required a common means of disconnect and that can be accomplished using two single pole breakers and a handle tie.Depending on what code cycle you are on, it would also require a 2 pole breaker since you are sharing the neutral.
Not an issue based on the OP using NM cable.The requirements for MWBC are onerous and it may be better to not use.
In addition to a two pole CB you may need to group the neutral and ungrounded conductors in the panel and all junction boxes.
See 200.4(B) and more importantly 210.4(D)
Some of the changes in requirements in the past 10-15 years on MWBC's are there to protect the untrained IMO.
(Other supply schemes and voltages, such as 208Y/120 three phase four wire, can also be used instead, but the MWBC must contain all of the phase wires plus a shared neutral.
Great description of MWBC and all their advantages. Pitty they are trying to take them away from us.In detail:
A three wire plus ground (2 hot, 1 neutral, + ground) MWBC can be used anywhere that you need to run two 120V circuits to the same general area of a building using a shared neutral to both reduce voltage drop and reduce cost. It can be contained in one cable (e.g. NM) or it can be run using separate wires in the same raceway. The source of the circuit described must be a 120/240 single phase three wire panel.
(Other supply schemes and voltages, such as 208Y/120 three phase four wire, can also be used instead, but the MWBC must contain all of the phase wires plus a shared neutral.
If you have two roughly balanced 120V loads, the current in the neutral wire will be small and so the voltage drop seen by the load will be roughly half that seen with two independent neutral 120V circuits.
And you will use less copper.
And for derating the ampacity of wires in a raceway the single three wire MWBC will count as only two current carrying conductors CCCs) while two independent circuits will count as four.
An example of a handle tie for Square D breakers:
(Note, this doesn't turn two breakers into a dual pole [common trip] breaker. It just forces the user to turn off both circuits at the same time).
There is nothing in the code that says you can't use two phases and the grounded conductor from a 3 phase system as a multiwire circuit. The only issue is, as you noted, the grounded conductor is a current carrying conductor.Why cant you run a 2 phases+neutral MWBC? I know the neutral would count as a CCC but other than that I am not aware of a restriction.
There is nothing in the code that says you can't use two phases and the grounded conductor from a 3 phase system as a multiwire circuit. The only issue is, as you noted, the grounded conductor is a current carrying conductor.
Note, however, that there are limitations on putting line to line loads on an MWBC that also supplies line to neutral loadsI agree, otherwise you wouldn't be able to hook up a 1Ø, 120/208 volt dryer or range.
Note, however, that there are limitations on putting line to line loads on an MWBC that also supplies line to neutral loads
See 210.4(C)Such as?
Note, however, that there are limitations on putting line to line loads on an MWBC that also supplies line to neutral loads
Such as?