G grumpy11 Senior Member Dec 4, 2010 #1 we are running a 3phase 4 wire plus an egc for 3 gfci receptalces . we intend to splice in a junction box above the location of each gfci and drop down the hot, neutral, and egc for each gfci receptale. would avoid neusance tripping
we are running a 3phase 4 wire plus an egc for 3 gfci receptalces . we intend to splice in a junction box above the location of each gfci and drop down the hot, neutral, and egc for each gfci receptale. would avoid neusance tripping
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Dec 4, 2010 #2 This will work fine. Just don't tie the neutrals on the load side for the different phases. Just keep the neutrals on the line side.
This will work fine. Just don't tie the neutrals on the load side for the different phases. Just keep the neutrals on the line side.