Am I understanding this correctly?
On a 240v single phase service in a house if 2 ungrounded conductors share a neutral and terminate on the same yoke of a receptacle approved handle tyes are required to disconnect both circuits 210.4b.but if the 2 ungrounded conductors feed loads that arent on the same yoke approved handle tyes are not required but the neutral must be made up to where disconnection of a device does not interupt the neutral path 300.13b.My question is if approved handle tyes are not used in the second instance you could shut 1 circuit off in the panel and disconnect the neutral from the neutral bar and have a load on it from the other circuit that is still energized if something is being used.(equally as dangerous)Am I missing something here?
On a 240v single phase service in a house if 2 ungrounded conductors share a neutral and terminate on the same yoke of a receptacle approved handle tyes are required to disconnect both circuits 210.4b.but if the 2 ungrounded conductors feed loads that arent on the same yoke approved handle tyes are not required but the neutral must be made up to where disconnection of a device does not interupt the neutral path 300.13b.My question is if approved handle tyes are not used in the second instance you could shut 1 circuit off in the panel and disconnect the neutral from the neutral bar and have a load on it from the other circuit that is still energized if something is being used.(equally as dangerous)Am I missing something here?