Multiwire circuits

Status
Not open for further replies.

mrswib

Member
If you have (4) 20A 120V linear load branch circuits (120/240V single phase service)going into a junction box,do the grounded conductors need to terminate at the panel or could you run one conductor to the junction box that would be sized at 40A?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Multiwire circuits

Why not state what you have found along with the article number that you think applies, and I'm sure will get feedback. Since you are preparing for an exam you need to do as much as you can to come up with the answer.

You may surprise yourself, and the feedback you get will be "You're right"

Roger
 

mrswib

Member
Re: Multiwire circuits

The reason I have asked the question is that I have never seen this done on Branch Circuits in all my years as an Electrician and unable to find a code that says it can not be done. The Example I used was not the best because the savings would be minimal. If there was 10 or 20 circuits involved the labor and material savings add up.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Multiwire circuits

Go to this thread for more than you would ever want to know about this subject. :D

You can also do a search and come up with more.

Roger
 

clt46910

New member
Re: Multiwire circuits

I seen this done once in some offices that we was tearing out for a remodel. From what I understood it has been there for a number of years and seemed to have worked Ok. Of course we did not repeat the same thing...LOL
 
G

Guest

Guest
Re: Multiwire circuits

Here is some reading that might interest you. Take it with a grain of salt as the author does have an agenda and the piece is 10-years old. Even if imperfect it should help you get your thinking cap on about Super Neutral.
Dispelling the Super Neutral Myth

Good luck on your exam! What exam are you taking?

[ October 27, 2003, 12:48 PM: Message edited by: awwt ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Multiwire circuits

Originally posted by clt46910:
I seen this done once in some offices that we was tearing out for a remodel. From what I understood it has been there for a number of years and seemed to have worked Ok. Of course we did not repeat the same thing...LOL
clt46910 Welcome to Mike Holt's Forum. :)

Why could you not repeat this installation? :)

Do you know a code article that prevents you from doing so? :)

Not giving you a hard time, this is just a subject that comes up once in a while here.
 