I have (2) 120 volt outdoor lighting circuits sharing a neutral with 12 amps on each phase. The run is 250'. Can this be calculated as a 240 volt circuit?
2x12.9x12x250/7.2
2x12.9x12x250/7.2
brian ploskunak said:Can this be calculated as a 240 volt circuit?
kevinware said:I am assuming this is a 120/208 three phase panel? What size are the phase conductors now? What is the wattage of the lights? 250' is a long way to go to be using 12AWG and stay with-in the NEC recommendations.
You can if the load is balanced for the 250 ft. If so, I get about 9 volts drop,brian ploskunak said:I have (2) 120 volt outdoor lighting circuits sharing a neutral with 12 amps on each phase. The run is 250'. Can this be calculated as a 240 volt circuit?
2x12.9x12x250/7.2
While they are line to neutral loads, if both loads are at the end of the circuit, there is no current flow in the grounded conductor and the circuit can be treated as a 240 volt circuit for the purposes of voltage drop.No. All your loads are line to neutral loads.
. . . which is why we say that a MWBC is more "efficient" than separate 2-wire circuits. The shared neutral effectively (and approximately) halves the voltage drop.don_resqcapt19 said:While they are line to neutral loads, if both loads are at the end of the circuit, there is no current flow in the grounded conductor and the circuit can be treated as a 240 volt circuit for the purposes of voltage drop.
In determining voltage drop you should always treat line to neutral loads as such even for mwbcs, unless it can reasonably be expected that all loads of the mwbc will always be concurrently on or off. This takes into account the worst case scenario where only one circuit is conducting.brian ploskunak said:Thanks guys for all the great input. I guess I need to decide if I treat it as a 120V load and go with #6 or a 240V load and go with #8. That's not a big differance, but I have (10) circuits like this to do. BTW, the wire has not been run yet. Sorry, if I gave the impression that it was already fed with #12.
infinity said:I'm curious as to why you would assume that this is fed from a 208 volt panel? This could be from a single phase 120/240 panel since the OP said 240 volts.
A classic example of what happens when you don't see what you read......
Smart $ said:In determining voltage drop you should always treat line to neutral loads as such even for mwbcs, unless it can reasonably be expected that all loads of the mwbc will always be concurrently on or off. This takes into account the worst case scenario where only one circuit is conducting.