zappy Senior Member Location CA. Jan 17, 2023 #1 I am working in a hospital, remodeling rooms etc. must I pull a neutral down to every switch now? Thank you for your help.
I am working in a hospital, remodeling rooms etc. must I pull a neutral down to every switch now? Thank you for your help.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jan 17, 2023 #2 It's by far not one of those "yes-no" answers. It varies by Code cycle and by then details of the exceptions. You really need to check 404.2 for the correct answer.
It's by far not one of those "yes-no" answers. It varies by Code cycle and by then details of the exceptions. You really need to check 404.2 for the correct answer.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jan 17, 2023 #3 The general rule is that you must supply a neutral unless the wiring method, such as conduit, allows for adding one if needed in the future.
The general rule is that you must supply a neutral unless the wiring method, such as conduit, allows for adding one if needed in the future.