True or false?
A multi-wire circuit (3 hot with common neutral)(for example serving receptacles in office cubicles) needs to be connected to a 3 pole circuit breaker.
True. 3 pole breaker or single pole breakers with handle ties
IMO the handle tie makes it mulitpole.Wouldn't the part in red make the question false?
False, as stated above see 210.15(B)(1)True or false?
A multi-wire circuit (3 hot with common neutral)(for example serving receptacles in office cubicles) needs to be connected to a 3 pole circuit breaker.
IMO the handle tie makes it mulitpole.
Absolutely right.Absolute not.
A multipole breaker is factory built with an internal common trip. With a multipole breaker a short circuit on one pole will always open all poles.
On the other hand two or three single pole breakers with handle ties will not open all poles due to a short on one pole. This is due to the required 'trip free' design of breakers.
True or false?
A multi-wire circuit (3 hot with common neutral)(for example serving receptacles in office cubicles) needs to be connected to a 3 pole circuit breaker.
True a 3 pole breaker can be the simontaneous disconnect
And just FWIW, a three pole circuit breaker does not HAVE to be common trip. Almost all of them are though.Still false. A 3 pole circuit breaker can be a simultaneous disconnect, but so can three single pole circuit breakers with a handle tie.
A 4 conductor mwbc does not NEED to be connected to a 3 pole circuit breaker.
And just FWIW, a three pole circuit breaker does not HAVE to be common trip. Almost all of them are though.
A single two pole breaker with handle ties but without common trip is often found as part of quad breaker sets.
Absolute not.
A multipole breaker is factory built with an internal common trip. With a multipole breaker a short circuit on one pole will always open all poles.
On the other hand two or three single pole breakers with handle ties will not open all poles due to a short on one pole. This is due to the required 'trip free' design of breakers.
Probably not (in terms of three pole low voltage consumer breakers.)Can you post an example?
Still false. A 3 pole circuit breaker can be a simultaneous disconnect, but so can three single pole circuit breakers with a handle tie.
A 4 conductor mwbc does not NEED to be connected to a 3 pole circuit breaker.
The my statement was true did not insinuate it was the only method availiable (can)
The answer to the OP's question cannot be both True and False. It is False.
Sure seemed like you were only responding to my statement as false when you used a partial quote. I thought I adressed the OP's statement with the skinning cat verbage as false which means there is more than 1 method to achieve the same goal.