I am looking for Cable Life expectancy chart/formula for 5KV, MV-90 non-shielded, EPR Insulation with PVC jacket and the appropriate life expectancy de-rating factors assocaited with cable loading (80% loaded, 100% loaded), temp, etc.
The original cable was installed in 1970, An addiditonal feeder was added when motor was upgraded in 1984/5. (8000hp compressor)
I was under the impression that 30-50 years is a typical life expectancy, but I can not find written confirmation.
I am also contacting cable vendors, (waiting for the reply)
I have found information on XLPE insulation but not on EPR.
I know motors and transformers have the 10 degC rule of thumb (Every increase in temp of 10 deg C halves the life expectancy)
The original cable was installed in 1970, An addiditonal feeder was added when motor was upgraded in 1984/5. (8000hp compressor)
I was under the impression that 30-50 years is a typical life expectancy, but I can not find written confirmation.
I am also contacting cable vendors, (waiting for the reply)
I have found information on XLPE insulation but not on EPR.
I know motors and transformers have the 10 degC rule of thumb (Every increase in temp of 10 deg C halves the life expectancy)