Has anybody seen AF rated MV switchgear used outdoors? This would be in an area that is far from any buildings or foot traffic.
Also, what are the typical provisions for retrieving the breaker out of the cubicle? I typically use the apparatus that comes with the swgr for inserting or removing the MV breakers but, that has always been inside a control house or aux building. I would assume that an outdoor application would at least require the concrete foundation to be extended to at least 6 feet in front of the cubicles.
Also, what are the typical provisions for retrieving the breaker out of the cubicle? I typically use the apparatus that comes with the swgr for inserting or removing the MV breakers but, that has always been inside a control house or aux building. I would assume that an outdoor application would at least require the concrete foundation to be extended to at least 6 feet in front of the cubicles.