MAK

Senior Member
I had an exam recently and there was a question about MV cable and it's application, specifically if it was a direct sunlight cable or not. I looked article 310 but did not find it. I'm lost. Where should I have looked?
Thanks.:grin:
 

mdshunk

Senior Member
Location
Right here.
Interesting. Some MV cable is exposed to the sun at the top of the riser where it terminates in a pothead. What was the test question, exactly? If it asked simply if it needed to be sunlight resistant if it's installed where the sun can get at it, that would be true.
 

mdshunk

Senior Member
Location
Right here.
MAK said:
The question was: true or false MV cable is rated for direct sunlight?
I could not find it in my NEC 2005.
I don't think the NEC gets into that, but I could be wrong. The manufacturer's make it both ways, with most of it being sunlight resistant, since it is stored outdoors on reels normally for months on end. MV-90 and MV-105 are both normally sunlight resistant, whether you ordered it that way or not.
 

mdshunk

Senior Member
Location
Right here.
MAK said:
So what is MV cable typically used for? I've never heard of it and some of the guys from work could not give me a satisfactory answer.
2400v and up, normally. It's in a lot of cable trays in industrial places.
 

celtic

Senior Member
Location
NJ
mdshunk said:
Thanks. I think it's safe to say that even though that's the "uses not permitted" paragraph, most or all of it is sunlight resistant now, and therefore permitted. That test question may well have been poorly worded.

I agree.
I guess the all encompassing 110.3(B) is the "out" in the real world...on the test, you have to go "by the book".

mdshunk said:
Here's your reward, Celtic, a nice song for you.
LMAO...what the heck is that?
 
Last edited:

celtic

Senior Member
Location
NJ
MAK said:
So what is MV cable typically used for? I've never heard of it and some of the guys from work could not give me a satisfactory answer.


I'm sure you heard of "4160"?
4160 is "slang" for 5Kv ~ or vice versa :grin:

Here is a 5kv switch gear:
gemvgr.jpg



The cable that feeds the bus will be MV.
Here is some MV cable:

249865.jpg


Some MV cable terminations:
c3-s.jpg



Another termination/application:
605ecmPQ1_small.jpg
 

mdshunk

Senior Member
Location
Right here.
MAK said:
I see 328.12
Not for use in direct sunlight.

Thank you gentlemen for your quick responses and the code reference. :D :)

Unless identified for the use, ... shall not be used... where exposed to direct sunlight.

There's no way to answer the test question without more information on the cable they're quizzing you about. This is the type of thing that ticks me off about some tests.
 

celtic

Senior Member
Location
NJ
mdshunk said:
Unless identified for the use, ... shall not be used... where exposed to direct sunlight.

There's no way to answer the test question without more information on the cable they're quizzing you about. This is the type of thing that ticks me off about some tests.


Poorly worded question, no doubt.
 

MAK

Senior Member
mdshunk said:
Unless identified for the use, ... shall not be used... where exposed to direct sunlight.

There's no way to answer the test question without more information on the cable they're quizzing you about. This is the type of thing that ticks me off about some tests.

In hind sight I see your point it could have been worded better to remove any confusion.
 

zog

Senior Member
Location
Charlotte, NC
Look on the roof any any large manufacturing plant and there are MV cables in direct sunlight everywhere, I could post hundreds of pics.
 