cah279
Member
- Location
- Wilkes-Barre
- Occupation
- Engineer
We have an installation at a new manufacturing plant where the Utility Company is Designing & Constructing a 20MVA Substation (69/4.16kV). Our demarcation point where we will pick up power, will be at their rigid bus structure after their secondary CB and disconnect switch in the substation. The plan is to then run below grade from their rigid bus via duct bank approximately 40’ so we can get outside of their substation fence. The utility company will provide the duct bank and raceway system and we will provide all cabling. Once outside the fence, we will rise vertically with rigid conduit to an overhead cable tray system 20’ in the air, and then extend via cable tray 600’ or so to our electrical room. Inside the electrical room, we’ll have cable tray as well where we then terminate on the top of our 3000Amp Switchgear Lineup (3000Amp MCB). So, our installation is approximately 600’ of Cable Tray, (2) risers via 5” Rigid Conduit (one in the substation to their rigid bus, one outside the fence up to our cable tray system) and about 40’ of underground duct bank that they will install.
We are trying to order cable and I’m looking at the following cable (per client’s spec) - 3/C, 5kv, 115 Mil, NL-EPR, 133% , MV-105, Cu Conductor Cable.
I’m somewhat confused on which 310.60(C) Table I should be following. Initially I keep getting pulled into 310.60(C)(79) b/c of my underground 40’ of duct bank to get out of the substation, but my trip up is when they start talking about One, Three and Six Circuits. Obviously looking at (6) circuits decreases my ampacity a lot. I was initially looking at running (6) Sets of 750kcmil to get my full 3000Amp bus rating per the above cable which has a 530Amp capacity per cable at 90degC (assuming I have to follow 110.40 for temperature limitations despite specifying MV-105 Cable).
Any thoughts or guidance would be appreciated. If I am leaving out any detail, let me know.
Thanks
We are trying to order cable and I’m looking at the following cable (per client’s spec) - 3/C, 5kv, 115 Mil, NL-EPR, 133% , MV-105, Cu Conductor Cable.
I’m somewhat confused on which 310.60(C) Table I should be following. Initially I keep getting pulled into 310.60(C)(79) b/c of my underground 40’ of duct bank to get out of the substation, but my trip up is when they start talking about One, Three and Six Circuits. Obviously looking at (6) circuits decreases my ampacity a lot. I was initially looking at running (6) Sets of 750kcmil to get my full 3000Amp bus rating per the above cable which has a 530Amp capacity per cable at 90degC (assuming I have to follow 110.40 for temperature limitations despite specifying MV-105 Cable).
Any thoughts or guidance would be appreciated. If I am leaving out any detail, let me know.
Thanks