I am working on a design build project that the contractor has installed C type conduit bodies in a 4" rigid conduit run. The conduit will have 3-1/0 15kV cables installed. I don't like the idea of the conduit bodies being used but need to find a viloation of some sort to get them to remove it and change to a pullbox. Has anyone run into this or have any input on this type of installation? I know its a fill factor violation but I wanted to list as many as I could.
Thanks in advance for any input.
That C fitting can only be used as a lubricating point in a cable pull.
The cable can not be bent to a radius of less than 7 times its diameter during installation if it is shielded with wire. The multiplier goes to 12 if the cable is shielded with foil or tape. So, if the cable diameter were 1.5 inches it can not be bent into a radius of less than 10.5 inches or a circle of less than 21". Do the math for tape shielded and you get a much larger radius or circle as your minimum.
These calcs only apply during cable pulling. The numbers are different for the final training of the cables. An example would be at the splice or termination points where a sharper bend is allowed.
Just looked up typical 1/0 15 KV shielded cable and found 1-1.1 inch diameter. Of course, actual diameter of cable must be used.