MV Cable Termination

Status
Not open for further replies.

E Torres

Member
I have a 5kv load break switch feeding a 150kva,3ph, 5kv/480/277V xfmr. My dilemma is that we are using MV cable and according to art. 300.40 I need to provide stress cones on all terminations, but I don't have enough room in the xfmr to install the stress cones. Anyone have any suggestions?
 
What kind of termination is in the transformer, live front? Most stress cones are only a couple of times the cable diameter, and not very long. It would seem uncommon for there to be no room in a primary compartment. You might set the transformer over a vault and enter from the bottom, that would give you a lot of room below the bushings.

Jim T
 
Xfmr

Xfmr

The xfmr terminations, both X and H, are at the front. X terminations are at the bottom and the H terminations are at the top of the core. The transformer is totally enclosed and is only 36" in height. We are running the MV cable up into a cable tray from the load break switch and into the transformer. I would think that the manufacturer would have known about this problem and would size the xfmr enclosure accordingly. :-?
 
Forum

Forum

Ed,

I am clad to see you use this forum. I have used it from time to time have and found it very useful. Let me know when you have worked out your problem.

Karl
 
Are the terminations deadfront (elbow connections required) or live front (stress cones required)? An elbow can be made up in a pretty small space. In either case if you do not have enough room you need a hand hole or a spacer under the transformer. The transformer manufacturer should offer a spacer that can bolt to the bottom to raise the terminals up enough to terminate the MV cables
 