I have an installation where I would like to route (2) 3/C #2 AWG, 1 #6 AWG Ground, EPR insulation 133%, Aluminum Interlocked Armor, UL Type MC, Shielded, 5 K V, MV-105, Copper, XLPE cables in a raceway that is embedded in a concrete cross beam on a paper machine dryer section. The cables are feeders for (2) MV motors.
The raceway is a 6" Schedule 40 PVC conduit, 22' long. The cables are routed to and from the raceway in a cable tray.
The OD of each cable is 1.75"
The total raceway fill calculates to 16.84%
Is there any code violations with this proposed routing?