MV cables passing through Car parking

Status
Not open for further replies.

TMMB

Senior Member
Location
EGYPT
Occupation
Electrical Manager
I HAVE MV CABLES ON TRAY/LADDER PASSING THROUGH CAR PARKING, THERE IS ANY REQUIRMENTS OR INSTRUCTIONS REQUIRED ACCORDING TO NEC , PLEASE ADVISE

Regards for all
 
392.18(H) Marking. Cable trays containing conductors rated over 600 volts shall have a permanent, legible warning notice carrying the wording ?DANGER?HIGH VOLTAGE?KEEP AWAY? placed in a readily visible position on all cable trays, with the spacing of warning notices not to exceed 3 m (10 ft).
 
I HAVE MV CABLES ON TRAY/LADDER PASSING THROUGH CAR PARKING, THERE IS ANY REQUIRMENTS OR INSTRUCTIONS REQUIRED ACCORDING TO NEC , PLEASE ADVISE

Regards for all
328.10 Uses Permitted. Type MV cable shall be permitted for use on power systems rated up to and including 35,000 volts, nominal, as follows:

(1)
spacer.gif
In wet or dry locations.

(2)
spacer.gif
In raceways.

(3)
spacer.gif
In cable trays, where identified for the use, in accordance with 392.10, 392.20(B), (C), and (D), 392.22(C), 392.30(B)(1), 392.46, 392.56, and 392.60. Type MV cable that has an overall metallic sheath or armor, complies with the requirements for Type MC cable, and is identified as ?MV or MC? shall be permitted to be installed in cable trays in accordance with 392.10(B)(2). S
 