Good morning,
I have a question about complying the NEC for the grounding of 4000V rated MV motor.
At this time we have the frame grounded at two points as it could be observe in the below sketch as per NEC 250.112(C) and 430.242.
The supply cable is 3P3W without equipment grounding conductor.
The connection to the frame, if it is not indicated by supplier, it has been done by experienced on-site people.
However, our client is claiming us to explain why is not connected any grounding conductor to the grounding terminal installed at inside the terminal box. This terminal box is factory mounted and it is keeping permanent metallic contact with the motor frame, so I understand that it is not necessary to connect the grounding terminal since the motor is already being grounded as per NEC 250.112(C).
The case is that the NEC 430.12(E) seems to require also the connection to the grounding terminal of the motor terminal box.
Question: How could I defend the current design by means of the NEC, which is considering no connection to the grounding terminal but to motorframe (see below sketch)?
Thank you very much in advance.
I have a question about complying the NEC for the grounding of 4000V rated MV motor.
At this time we have the frame grounded at two points as it could be observe in the below sketch as per NEC 250.112(C) and 430.242.
The supply cable is 3P3W without equipment grounding conductor.
The connection to the frame, if it is not indicated by supplier, it has been done by experienced on-site people.
However, our client is claiming us to explain why is not connected any grounding conductor to the grounding terminal installed at inside the terminal box. This terminal box is factory mounted and it is keeping permanent metallic contact with the motor frame, so I understand that it is not necessary to connect the grounding terminal since the motor is already being grounded as per NEC 250.112(C).
The case is that the NEC 430.12(E) seems to require also the connection to the grounding terminal of the motor terminal box.
Question: How could I defend the current design by means of the NEC, which is considering no connection to the grounding terminal but to motorframe (see below sketch)?
Thank you very much in advance.