MV parallel feeders; EGC required per conduit?

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Do I need to run an EGC for each set of 15kV, 1-C shielded cable, (3 per phase, 500kCMIL) paralleled in underground PVC conduit?


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Tape shield cannot be used as an EGC for solidly grounded systems. I don't see anything in part X of 250 that modifies the typical rule of running an EGC in each parallel conduit.

This system is not solidly grounded. There’s a NGR in the transformer neutral bushing; 400A, 20 ohm.


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
In that case I think you can use the tape shield as the EGC if it's rated for the clearing time other protective device without damaging it. Not sure how exactly you determine that though.

Exactly my thoughts. Protective relaying will ‘clear’ the fault via the cable shielding before damage to the cable occurs, therefore an additional EGC is not required. These are outdoor, substation type power transformers that feed a very large industrial plant.
Many thanks!
Isaiah


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
In that case I think you can use the tape shield as the EGC if it's rated for the clearing time other protective device without damaging it. Not sure how exactly you determine that though.

The cables emerge from grade and attach directly to an outdoor substation type motorized disconnect switch. Where do I land the shields? Also, I assume only one end needs to be grounded? The opposite cable end terminates at MV switchgear MCB several hundred feet away.


Sent from my iPhone using Tapatalk
 

yesterlectric

Senior Member
Location
PA
Occupation
Electrician
The cables emerge from grade and attach directly to an outdoor substation type motorized disconnect switch. Where do I land the shields? Also, I assume only one end needs to be grounded? The opposite cable end terminates at MV switchgear MCB several hundred feet away.


Sent from my iPhone using Tapatalk
This type of an installation is one in which there should be a detailed plan from an engineer that would make this clear for the installer. An installer who didn’t get this in a drawing or specifications package is entitled to receive it.

The NGR and grounding xfmr systems I’ve had on my projects have either concentric neutral or a ground wire. But again, this level of specifics of installation should be provided to the installer.
 
The cables emerge from grade and attach directly to an outdoor substation type motorized disconnect switch. Where do I land the shields? Also, I assume only one end needs to be grounded? The opposite cable end terminates at MV switchgear MCB several hundred feet away.


Sent from my iPhone using Tapatalk
I dont really know those details. My MV knowledge is limited. I think shield currents need to be taken into account and there are times when you only want to ground one end of the shield - but I dont know much more than that. I am more familiar with MGN systems with CN cables.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
This type of an installation is one in which there should be a detailed plan from an engineer that would make this clear for the installer. An installer who didn’t get this in a drawing or specifications package is entitled to receive it.

The NGR and grounding xfmr systems I’ve had on my projects have either concentric neutral or a ground wire. But again, this level of specifics of installation should be provided to the installer.

But the relay will trip on just a few cycles before cable is damaged using the shield only


Sent from my iPhone using Tapatalk
 