This is a bit of an odd ball situation. I am not really seeing any reason not to proceed in either way. Any thoughts? ....
I have four 5" conduits in a duct bank by themselves. I have a A-B-C phases and ground to run using 1000kcmil wire, medium voltage, each phase has four parallel runs, and run a full size 350 ground in each conduit. Both options gives me a fill % of 39.0% which is just under the 40% allowed.
Option 1: Run 1 parallel run A-B-C-g in each conduit, so four sets, side by side (A-B-C-g, A-B-C-g, A-B-C-g, A-B-C-g,)
Option 2: Run 3 parallel runs of each phase per conduit for 3 conduits (A-A-A-g, B-B-B-g, C-C-C-g) then the fourth conduit run A-B-C-g.
Running separately is allowed per 310.10(H)(3) as long as 2-6 are followed and I believe they are.
Thoughts?
Thank you for your time.