I'm looking at a new installation where a 500MCM 34.5kV SE feeder will be fed from an existing OH 34.5kV utility line to a new MV Switchgear lineup. The riser pole where the connection will be made will have a gang switch. The gang switch serves as the point of demarcation between utility and owner with cable after the switch belonging to owner.
The 34.5kV OH line appears to have a shield wire which is connected to a solid copper ground wire at each of the poles which runs down the pole to ground.
There is an existing riser pole on the site and it appears that there are only (3) phase conductors coming up the riser pole and no grounded conductor. The shields at each of the cable terminations are all connected to the ground wire running up the pole.
My question is in this type of SE application if the grounded conductor is required? Since there is nowhere on the pole or OH line to connect the grounded conductor to I'm assuming that is is not required and that only the cable shield is connected to ground points at both the riser pole and switchgear?
The 34.5kV OH line appears to have a shield wire which is connected to a solid copper ground wire at each of the poles which runs down the pole to ground.
There is an existing riser pole on the site and it appears that there are only (3) phase conductors coming up the riser pole and no grounded conductor. The shields at each of the cable terminations are all connected to the ground wire running up the pole.
My question is in this type of SE application if the grounded conductor is required? Since there is nowhere on the pole or OH line to connect the grounded conductor to I'm assuming that is is not required and that only the cable shield is connected to ground points at both the riser pole and switchgear?