I do not have experience with primary metered systems, where the transformer is customer owned and the service disconnect is on the primary side of the transformer.
- For purposes of meeting the service disconnect and OCPD requirements of 230.205 and 230.208 ? do the optional load break switches and fusing available from the xfmr mfr provide this function (are they service rated) or is a separate switchgear assembly required? IF separate, does this normally take the form of a padmount switch? And if a separate padmount switch is installed, is there any need for a load break switch on the transformer?
- For supply to a delta primary, from a MGN utility feed, my understanding is 250.24(C) does not apply (>1000V). I see nothing in 250 requiring me to bring the grounded conductor to the service equipment. If there is no grounded conductor, it is not clear to me what the requirements for bonding are at the service disconnect ? I am not understanding the requirements of 250.186(B) ? is this saying a conductor must be run with the service conductors?