Re: MV / Substation grounding
Current in substation ground grids and industrial ground systems is very common. Some of it is induced current - the ground grid, building steel and bonding jumpers can form low impedance ground loops. If a high ampacity circuit is nearby, currents can be induced in the loops.
Also, the complete high voltage system has some capacitance to ground, supposedly about equally balanced between phases. All of the cable, bus, and transformer insulation on the system is just like a big capacitor with the hot phase wire as one lead and ground as the other. If the phases are not perfectly equal, some charging current will flow in the neutral to ground connection.
Current can be measured in most capacitor bank neutral/ground connections. Caps are usually wired in a wye, phase to ground with the capacitor case connected to ground. If there is any third harmonic noise in the system, 3rd harmonic current has a path to flow to ground through the capacitors. The amp meter may not differentiate between 60 Hz & 180 Hz currents. Also any difference in voltage across the caps or in the capacitance values will make unequal phase currents flow. If curents are not equal, they can't add up to zero in the wye connection and end up flowing in the ground connection.
Cable shield grounds can have currents induced by the cable current. The power current in the cable induces a voltage in the shield which forces currents to flow if both ends of the shield are ground. The Okonite website had some good articles on this. One solution is to only ground the cables at one end.