Looking at a project in a substation for renewable site where the 34.5kV delta side of GSU feeds a 34.5kV switchgear lineup. The switchgear lineup which serves the site collector feeders also feeds a zig-zag grounding transformer which derives the grounding reference for the 34.5kV system.
My question is in this application what are the equipment ground conductors between GSU secondary and switchgear considered? Usually with a wye grounded transformer for a SDS these are considered supply side bonding jumper and sized in accordance with 250.102. Would these still be considered supply side bonding jumper, or would these be considered equipment grounding conductor or something else?
My question is in this application what are the equipment ground conductors between GSU secondary and switchgear considered? Usually with a wye grounded transformer for a SDS these are considered supply side bonding jumper and sized in accordance with 250.102. Would these still be considered supply side bonding jumper, or would these be considered equipment grounding conductor or something else?