bcorps
Member
- Location
- Evansville, IN
- Occupation
- Engineer
I have a 12,470V (7.2kV to ground) enclosed bolted pressure switch on a campus. The front is completely unobstructed. They are installing a generator behind it, inside a wooden concealing fence; i.e. no "live or grounded" obstructions towards the back of the switch. So, my first take is that electrically speaking (Table 110.34(A)), it only needs 30 inches between the back of the switch enclosure and the fence. However, the owner is saying it requires extra clearance because the enclosure has a charging handle through the side of the enclosure, and it could "kick" while trying to open/close it. They're suggesting 5 feet working clearance, but honestly, I've never run across a specific required number for clearance needed to physically operate a switch...based on pure mechanical characteristics alone.
Any experience with this?
Any experience with this?