Mr. Chippers
Member
- Location
- Illinois
- Occupation
- Electrical Engineer
Customer is looking to replace a medium voltage transformer that is well past it's end of life date. Transformer gets extremely hot. It is installed in a supervised location. I was provided as-built drawings for reference. My question is, is the existing transformer even sized properly for the amount of load on the secondary?
Information is as follows:
Transformer: 2000kVA, 13.2kV-480Y/277V,3ph,4w, Z:5.62%
Primary OCPD: 150E fuse
Primary feeder size unknown
Secondary feeder consists of (8) 4"C, 4#535kCMIL & 1#4/0gd (diesel locomotive cable), type RHW, 90degC which goes into a tap box and connects to a 3000A busway to the switchboard
Switchboard: 3000A-3P LSIG MCB, 3000A swbd
Switchboard Load: Connected load = 6192.3A, Demand load = 2753.7A
Based on the transformer size, I calculated the rated currents as Ip=87.48A and Is=2405.63A.
Using NEC 450.3(A):
1. The primary fuse is within 300% requirement.
2. The secondary breaker is within the 250% requirement.
How can the transformer rated current be less than the demand load? I feel this could be why the transformer is hot all the time. Is this to code?
Information is as follows:
Transformer: 2000kVA, 13.2kV-480Y/277V,3ph,4w, Z:5.62%
Primary OCPD: 150E fuse
Primary feeder size unknown
Secondary feeder consists of (8) 4"C, 4#535kCMIL & 1#4/0gd (diesel locomotive cable), type RHW, 90degC which goes into a tap box and connects to a 3000A busway to the switchboard
Switchboard: 3000A-3P LSIG MCB, 3000A swbd
Switchboard Load: Connected load = 6192.3A, Demand load = 2753.7A
Based on the transformer size, I calculated the rated currents as Ip=87.48A and Is=2405.63A.
Using NEC 450.3(A):
1. The primary fuse is within 300% requirement.
2. The secondary breaker is within the 250% requirement.
How can the transformer rated current be less than the demand load? I feel this could be why the transformer is hot all the time. Is this to code?